Unread postby Clouseau2 » Tue 26 Jul 2005, 16:49:18

I think most houses in the US get 220 v, it just gets split. Someone with a better knowledge of electrical systems can explain the details. I thought we basically had the same system as other countries, it's just that we (USA) downgrade some the outlets we plug the majority of our equipment into whereas 220v countries do not.

It's been over 10 years since I took EE and I failed it the first time around, ha!
User avatar
Clouseau2
Lignite
Lignite
 
Posts: 262
Joined: Mon 18 Oct 2004, 03:00:00
Location: San Francisco, CA

Re: 110v or 225v electricity?

Unread postby Daculling » Tue 26 Jul 2005, 16:51:51

$this->bbcode_second_pass_quote('lotrfan55345', 'A') map of the world electricity voltages:
World Standards
175 countries use 225v and 39 use 110v. Is there an advantage/disadvantage to using 225v or 110v?
What has better efficiency/less losage?

You don't have 220 in your house? Take a closer look, I bet you have both. What voltage does you A/C or clothes drier run on?
Daculling
Heavy Crude
Heavy Crude
 
Posts: 1228
Joined: Tue 12 Apr 2005, 03:00:00

Unread postby MD » Tue 26 Jul 2005, 17:03:45

actually, the peak-to-peak voltage in both cases is approximately 340 volts. 115 is the root-mean-square(average) voltage of single phase, 230 is the root-mean-square of dual phase, 180 electrical degrees apart.
In fact, if you measure from the "hot" prongof one plug in your house to the "hot" prong of another, you may actually read 230 vac.
Back to efficiency. Higher voltage is more efficient at installation because it takes half the copper to transport the same power when the voltage is doubled.
Stop filling dumpsters, as much as you possibly can, and everything will get better.

Just think it through.
It's not hard to do.
User avatar
MD
COB
COB
 
Posts: 4953
Joined: Mon 02 May 2005, 03:00:00
Location: On the ball

Unread postby lotrfan55345 » Tue 26 Jul 2005, 18:03:48

$this->bbcode_second_pass_quote('', 'Y')ou don't have 220 in your house? Take a closer look, I bet you have both. What voltage does you A/C or clothes drier run on?

I just looked and actually I do. :)
So then it almost doesn't matter if its 110 or 220 because whats used to transport it to long distances is much higher anyway.
BUT, with all those transfromers, how much power is lost through those?
lotrfan55345
Heavy Crude
Heavy Crude
 
Posts: 1091
Joined: Tue 20 Jul 2004, 03:00:00
Location: Minneapolis / Pittsburgh

Unread postby Jaymax » Tue 26 Jul 2005, 18:42:57

Wikipedia
$this->bbcode_second_pass_quote('', 'O')riginally Europe was 110 V too, just like Japan and the US today. It was deemed necessary to increase voltage to draw more power with reduced loss and voltage drop from the same copper wire diameter. At the time the US also wanted to change, but it was deemed too costly to change all of the existing infrastructure.
Doomerosity now at 2 (occasionaly 3, was 4)

Currently (mostly) taking a break from posting at po.com. Don't trust the false prophets of doom - keep reading, keep learning, keep challenging your assum
User avatar
Jaymax
Lignite
Lignite
 
Posts: 259
Joined: Thu 16 Jun 2005, 03:00:00
Location: England

Unread postby ChumpusRex » Tue 26 Jul 2005, 19:04:45

$this->bbcode_second_pass_quote('', 'B')UT, with all those transfromers, how much power is lost through those?

It's a significant amount, but less than you might think.
Estimates vary, but for a large spread-out grid like the US power grid, efficiency is estimated at about 90-92% from power station to customer. For smaller, more densely populated countries (like Europe) it's slightly higher. For huge countries, like China or Russia, it's lower.

Transformers vary in efficiency - in general the massive house-sized things at power stations are more efficient than the smaller pole-mounted transformers. Additionally, more modern transformers are more efficient than older ones.
Pretty much all utility transformers have efficiencies of over 98% - the exceptions are small single-house transformers for remote farm-houses. A modern medium-size distribution transformer (enough for about 100-200 homes) can get an efficiency of about 99.4 - 99.5%. The biggest ones can get 99.8 %.
User avatar
ChumpusRex
Peat
Peat
 
Posts: 100
Joined: Mon 18 Jul 2005, 03:00:00

Unread postby Caoimhan » Tue 26 Jul 2005, 21:18:00

When we start using plug-in hybrids or pure battery-electric vehicles, it'll be 220V chargers most of us will use to start, because our houses have those 220V circuits.

I wonder what amperage they usually run at. 40? 60? 80?
User avatar
Caoimhan
Tar Sands
Tar Sands
 
Posts: 557
Joined: Tue 10 May 2005, 03:00:00

Re: 110v or 225v electricity?

Unread postby ubercynicmeister » Tue 26 Jul 2005, 22:21:36

$this->bbcode_second_pass_quote('lotrfan55345', 'A') map of the world electricity voltages:
World Standards
175 countries use 225v and 39 use 110v. Is there an advantage/disadvantage to using 225v or 110v?
What has better efficiency/less losage?

We (in Australia) use 240 v AC at 50 Hertz, as this is said to give fewer "brown-outs". The reason?
A 24 volt drop on 240 v is 10% of the supply.
A 24 volt drop on a 110 volt supply is (about) 22% drop.

I can only say that, like everyone ELSE has said here - the higher the voltage, the higher the transmission efficiency.
I can't add much to this column, sorry, but I find it interesting.
User avatar
ubercynicmeister
Tar Sands
Tar Sands
 
Posts: 640
Joined: Sun 25 Jul 2004, 03:00:00
Location: Hunter Valley, New South Wales, Australia
Top

Unread postby Daculling » Tue 26 Jul 2005, 22:31:51

$this->bbcode_second_pass_quote('Caoimhan', 'W')hen we start using plug-in hybrids or pure battery-electric vehicles, it'll be 220V chargers most of us will use to start, because our houses have those 220V circuits.
I wonder what amperage they usually run at. 40? 60? 80?

My A/C curcuit is at 50amp... but your's may be different depending on your equipment. The transformers at the poles have their own breaker... no clue what those are. While the 220 might be more efficient... if you ever got a hold of 220 you may appreciate inefficiently a bit 8O And 60hz is the worse for you cardio system BTW.
Daculling
Heavy Crude
Heavy Crude
 
Posts: 1228
Joined: Tue 12 Apr 2005, 03:00:00
Top

Unread postby pea-jay » Wed 27 Jul 2005, 02:48:37

Having lived in both Europe and the US, I have had 220V and 110V appliances and appliance sized transformers so that our US appliances ran in Europe and our European appliances ran in the the US. In Europe we had to have these step down transformers (not those cheapie travel sized ones, but those car battery sized, non electronic versions) or we would fry our appliances. In the us we simply reversed the terminals on the transformer and boosted the voltage or utilized the 220 dryer circuit which wasnt being used.

When my parents moved to the Philippines in 1993, they lived in a house that had 120/240 service to almost every room (dual wired). The funny thing about it was that all US style outlets were 240 and all Euro style outlets were 120. My dad spent the first weekend reversing all of them so he didnt fry all of the appliances.

Finally, right here in CA, I have metered my power and have seen the voltage as low as 107V and spiking as high as 128V (on a consistent basis). The current problems fried my CPU on my last computer, which is why I only use a UPS now. Bastards.
UNplanning the future...
http://unplanning.blogspot.com
User avatar
pea-jay
Heavy Crude
Heavy Crude
 
Posts: 1547
Joined: Sat 17 Jul 2004, 03:00:00
Location: NorCal

Unread postby Devil » Wed 27 Jul 2005, 07:28:16

Easily seen there are no engineers here. :)
There is no way that voltage changes could fry a CPU as the voltages from the PSU are stabilised. OTOH, they could fry the PSU. Aren't you confusing CPU and PSU?
The 110 V is from phase to neutral in the US. The 220 V in the US is from phase to phase of a 2-phase system. It is dangeous to use a single phase 220 V appliance across 2 phases, unless it has been specifically designed for it. It is probable that doing so may invalidate your fire/accident insurances.

The European 230 V is also from phase to neutral but of a 400 V 3-phase system. Our storage heater circuits are 3-phase star connections (delta connections would be less safe), but the rest of the house is on one single phase. It may be dangerous putting a US 220 V appliance on a European single phase circuit (inadequate insulation).
The choice of voltage for household use is a compromise between safety (electrocution), safety (fire), IR losses, cost of copper, cost of insulation etc. Low voltage = less risk of electrocution, more risk of fire, higher ohmic losses, more copper in the wiring but thinner insulation.
Devil
User avatar
Devil
Tar Sands
Tar Sands
 
Posts: 816
Joined: Tue 06 Jul 2004, 03:00:00
Location: Cyprus

Unread postby pea-jay » Wed 27 Jul 2005, 23:25:47

Yep, I meant power supply. It may as well fried the motherboard itself though, since the power supply on my was long since out of manufacture. No functioning PSU, no CPU. Oh well, it WAS out of date...
UNplanning the future...
http://unplanning.blogspot.com
User avatar
pea-jay
Heavy Crude
Heavy Crude
 
Posts: 1547
Joined: Sat 17 Jul 2004, 03:00:00
Location: NorCal

Unread postby mistel » Thu 28 Jul 2005, 19:05:46

$this->bbcode_second_pass_quote('ChumpusRex', '')$this->bbcode_second_pass_quote('', 'B')UT, with all those transfromers, how much power is lost through those?

It's a significant amount, but less than you might think.
Estimates vary, but for a large spread-out grid like the US power grid, efficiency is estimated at about 90-92% from power station to customer. For smaller, more densely populated countries (like Europe) it's slightly higher. For huge countries, like China or Russia, it's lower.
Transformers vary in efficiency - in general the massive house-sized things at power stations are more efficient than the smaller pole-mounted transformers. Additionally, more modern transformers are more efficient than older ones.
Pretty much all utility transformers have efficiencies of over 98% - the exceptions are small single-house transformers for remote farm-houses. A modern medium-size distribution transformer (enough for about 100-200 homes) can get an efficiency of about 99.4 - 99.5%. The biggest ones can get 99.8 %.

Its been a few years since college, and I would have to get out the old text books, but I think you are way off with the efficiency numbers. You have to look at all the parts of the system, Transmission line losses, transformer efficiency, etc,and multiply them to get overall efficiency. We did the calculation in school, (5 years ago!) and I remember it to be around 30%. If they could perfect super conducting transmission lines, there are huge efficiencies to gain.
I will try to find some numbers to back this up
User avatar
mistel
Peat
Peat
 
Posts: 137
Joined: Sun 20 Mar 2005, 04:00:00
Top

Unread postby ChumpusRex » Thu 28 Jul 2005, 20:13:45

$this->bbcode_second_pass_quote('', 'W')e did the calculation in school, (5 years ago!) and I remember it to be around 30%. If they could perfect super conducting transmission lines, there are huge efficiencies to gain.

If you include generation losses (i.e. the energy lost when generating electricity from burning coal) then 30% is reasonable, although rather pessimistic for technology in use today.
I have got some hard figures - e.g. UK's National grid achieved an efficiency of 98.25% in 1997/98 (latest figures I have to hand), but note that only includes the main national grid - which connects power stations to towns and big heavy industrial customers (e.g. steel works). Not counted are the losses coming from distributing electricity within the towns, which are likely to be similar (or slightly greater) than the main long-haul transmssion.

I have checked transformer efficiencies with manufacturers' technical documentation and believe them to be correct.
Superconducting transmission lines and transformers are an interesting technology, but the improvements are only likely to be incremental, if there are any at all - cryo-coolers need a lot of energy to run.
User avatar
ChumpusRex
Peat
Peat
 
Posts: 100
Joined: Mon 18 Jul 2005, 03:00:00
Top

Selling Power to the Power Grid-

Unread postby Kylon » Sat 27 May 2006, 02:32:51

Hello, I was wondering if any of you have any experience selling to the power grid from your own private generators.

I'm interested because very soon I may be able to produce a surplus amount of power, which I can sell to the power companies.

However, I talked to my father about this, and he said that if you try to sell power to large companies, they will hit you with a frivalous lawsuit, in order to tie you up in court, and eventually shut you down. Even though the law is on your side, he said the average court cost for those entering the business is about 6 million dollars. Even though they lose(do to the fact that what your doing is perfectly legal), ultimately, they tie up your resources for so long, and create such court cost, that you either back out, or go broke.

Anyway, does anyone have any experience selling power to the power companies?

Also, I was wondering, if they did a case against me, and I was technically not incorporated, but rather a sole proprietarship, could I be eligible for a public defender, that would fight the case for me, and therefore use the public courts legal resources, thus eliminating the ability of big corporations to destroy me with court cost?

Any assistance when it comes to knowledge in these matters would be much appreciated.
User avatar
Kylon
Expert
Expert
 
Posts: 836
Joined: Fri 12 Aug 2005, 03:00:00

Re: Selling Power to the Power Grid-

Unread postby AQIUS » Sat 27 May 2006, 02:44:08

hello

your topic caught my interest, and I can give you some info re the legal system: most states only appoint a public defender if you are charged with a criminal offense & you claim you are broke.
Even then, the state could keep track of the expense of the public defender and force you to sign an agreement to pay back the amount at a later date, or a nominal charge, before assigning one to your case.
Bear in mind that this all applies to criminal charges, and not civil cases, where your case might go.
I'm not a lawyer / this is not legal advice so relax all you JD's, just relaying some personal experience.
AQIUS
 

Re: Selling Power to the Power Grid-

Unread postby Kylon » Sat 27 May 2006, 02:56:11

Thank you for your assistance, I was afraid that might be the case.
User avatar
Kylon
Expert
Expert
 
Posts: 836
Joined: Fri 12 Aug 2005, 03:00:00

Re: Selling Power to the Power Grid-

Unread postby Micki » Sat 27 May 2006, 04:55:56

I thought the easiest and fully legit way of selling was to sell it to the electricity company. That should not result in any legal issues.
Try contacting some of your local elec utilities companies and see what they have to say.
Micki
 

Re: Selling Power to the Power Grid-

Unread postby miraculix » Sat 27 May 2006, 05:32:30

Kylon

it all comes down to where you are located

I presume somewhere in the good 'ol US of A

If that is the case you need to start talking to your city officials first, trying to get a feeling for what kind of regulations they have on their books.

Next step is to contact the PR office of your local utility company and ask them some hypothetical questions.

Say you are doing research for a school project or so and want to know something about that subject - try to get a written statement

Then contact your state government - write to the appropriate office for energy issues.

After making this round you may be more confused, but depending on your locale you may have some answers.

There are huge differences among states and even from county to county.

I am afraid if you end up being sued - you will be all on your own.

Maybe there is some advocacy group that may support you - I think there is - just search the web.

If you are not in the US things might be a lot easier.

Many countries in Euope have supportive legislation forcing the utility companies to pay entities that feed into the grid retail rates for the energy provided
User avatar
miraculix
Peat
Peat
 
Posts: 158
Joined: Tue 11 Apr 2006, 03:00:00

Re: Selling Power to the Power Grid-

Unread postby Frank » Sat 27 May 2006, 08:11:01

Most (if not all) States have net-metering requirements and are required to purchase excess power (usually generated by PV) from consumers. Requirements vary based on how much you're thinking of selling but unless you're a very large generator you shouldn't have any problem getting an agreement. It's generally very straightforward.

Call you utility and ask about net-metering; if they don't know then look at:

http://www.dsireusa.org/ for details on your State.